Motor question: 2hp 115/230v on a normal house outlet?

I just bought a KMG and it came with a motor. Its 2hp 115/230V. I cannot do any rewiring on my apartment building, so is there any way to step this thing down so I can use it in a normal 110V plug? If I am thinking right, this would currently need 20amps at 110v, which is too high unless I am wrong. What can I do? Am I up a creek? I am an electrical moron, and literally know nothing. The motor owner says I just change the "taps" and I can run it no problem, but that it will draw 20 amps.

I understand it will draw the most amps on startup, but I do NOT want to burn my building down. I also do not necessarily want to buy a new motor......

What are my options? Can i run a line down to my basement and plug it into a dryer outlet?

Someone enlighten me or provide me a "electrical instruction for morons" link.
Reply With Quote
  #2  
Old 09-09-2005, 02:55 PM
Jamey Saunders's Avatar
Jamey Saunders Jamey Saunders is offline
Moderator
 
Join Date: Jul 2002
Location: Portal, GA - If you know where it is, you probably got a speeding ticket.
Posts: 1,951
Send a message via AIM to Jamey Saunders Send a message via MSN to Jamey Saunders Send a message via Yahoo to Jamey Saunders
110 and 115 is the same thing. Po-tay-toh, Po-tah-to. As long as it's wired for 110/115, and you have a sufficient breaker you'll be fine. The amperage that you see on the motor for each voltage is it's rated amperage. Under no load, it'll draw about half that. Under load, it'll vary from half to the total rated amperage. Anything over the rated amperage can damage the motor.


__________________
Jamey Saunders -- Charter Member, GCKG
(Got a question? Have you tried to for the answer?)

"I won't be wronged, I won't be insulted, and I won't be laid a hand on. I don't do these things to other people, and I require the same of them." --John Wayne, in The Shootist
Reply With Quote
  #3  
Old 09-09-2005, 03:02 PM
cricket's Avatar
cricket cricket is offline
Steel Addict
 
Join Date: Aug 2005
Location: Alpharetta, Ga.
Posts: 256
Thumbs up

I believe your OK as long as your motor is wired for 115v. The motor is made to be wired for either voltage, just pay attention when you first turn it on, as long as you don't trip your breaker everytime you start it up, you should be good to go. The only other problem might be, if you have a heavy hand with the grinder, it might trip your breaker from time to time. You may have to use a lighter touch or install a bigger breaker.


__________________
Remember... hit it while it's HOT!!!
Reply With Quote
  #4  
Old 09-09-2005, 03:45 PM
TikTock's Avatar
TikTock TikTock is offline
Skilled
 
Join Date: Jan 2005
Location: Plaistow, NH
Posts: 562
Okay. I checked and my breaker is 15....I am not heavy at all while grinding. I used to grind on my 2X42 without it even bolted to the table. I usually let the belts do most of the work. So worst case scenario is it trips the breaker every time i turn it on, in which case I need to rethink the whole thing.....

Any problem with drilling a hole in the floor and running a 10' cord down to a dryer hookup? Those are on a 30 amp breaker....

Obviously im pulling at threads here....I need to make this work
Reply With Quote
  #5  
Old 09-09-2005, 06:13 PM
pjelect pjelect is offline
Steel Addict
 
Join Date: Sep 2004
Location: Madison, Ohio
Posts: 207
First, check the size of the wire attached to your 15A circuit breaker. Every once in awhile I see a 15A CB with #12 wire run to it. If the wire is #12 then change the CB to a 20A. If the wire is only #14, then leave it alone. As for using the dryer circuit, it's hoaky to do it that way. Cords should not be run through bored holes in the floor. That and a couple of other code violations you would create are not worth it. If the dryer receptacle is only 10' from your grinder, then the panel can't be too far away. Check and see if it has a spare opening in it. If so, run a dedicated 20A circuit up to your grinder. If all else fails call a #######d electrician to check it out. Sometimes the good ones(myself included) can spot an easy affordable solution to your problem.
Good luck! Pat McGroder
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -5. The time now is 11:25 PM.




KNIFENETWORK.COM
Copyright © 2000
? CKK Industries, Inc. ? All Rights Reserved
Powered by ...

Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
The Knife Network : All Rights Reserved