Thread: Grinder issue
View Single Post
  #12  
Old 07-15-2015, 11:47 PM
DanCom's Avatar
DanCom DanCom is offline
Skilled
 
Join Date: Sep 2013
Location: Leduc County, Alberta, Canada
Posts: 314
Red status LED is overload/I2t/short circuit according to the manual. Slow flashing green is normal.

A typical TEFC motor requires plenty of air flow and slowing the motor can greatly reduce cooling. I'd venture to guess the heat is building up as a result of the motor's fan not moving enough air at the slower speeds.

It appears you may have to have someone take a look at the VFD. Have them measure from terminals P1 to P2 for steady voltage DC when running. This will range from 0-5 volts and will go up and down when rotating the speed pot. If it's steady, then randomly jumping up and down or dropping to 0 V for no reason the pot is likely faulty. More common to see a failure with moving parts such as pots and switches. Have them also check the FOR /REV switch.

Wishing you speedy troubleshooting,

Dan